Dear Valued Customer,
As you are aware, over the weekend the 8th floor of PEER 1’s Toronto data center located at 151 Front Street experienced a fire with a UPS cabinet that set off a chain of events that resulted in power outages in multiple suites and network outages in others. I have detailed the events below.
PEER 1 is extremely thankful that no one was injured during the fire. The fire itself was contained within a single UPS cabinet and the Toronto fire department was able to extinguish it with the use of dry chemicals. No water was used, which significantly reduced the damage and aided in our ability to restore services to all data centers as quickly as possible.
I was personally involved in PEER 1’s response to the situation, and would like to take a moment to apologize to you for the information contained within our first few email alerts regarding the outage. When we were first organizing the team, we received an early report from our on-site staff that all power was out at 151 Front Street. That was not accurate. The fire caused a power outage in PEER 1’s suite 802. The local fire department cut power to PEER 1’s suite 709 as a preventative and safety measure to contain and extinguish the fire. The network gear providing connectivity for Suite 816 are kept in a cage in Suite 802. As a result, Suite 816 suffered a network outage. Power in the rest of the building was unaffected throughout the incident. There is a fine balance to providing information during a crisis, and we do our best to make sure updates to our customers are, quick, transparent, and accurate. In no way would we try to misrepresent the situation.
PEER 1 manages all of the equipment it provides to customers with safety and performance in mind. The UPS mentioned above has been in service for approximately four years. Its last service inspection was on July 2nd and it was only at 65% load. We do not yet have the root cause, but there was nothing in the unit’s maintenance record to indicate there was potential for a problem. Our service contractor and manufacturer are both involved in the investigation.
As part of the process to restore power quickly, we had to bypass the affected UPS. This means that suite 802 is running without UPS power until we can schedule delivery and replacement. We will expedite the process and keep customers in this suite up-to-date with the latest information on the timeline.
Outage Details:
(Timelines represent impact to “most” clients. Some specific network devices failed due to power loss and restore took longer.)
· Suite 802 – Power and network outage. Start 23:32PT End 03:10PT
· Suite 816 – Network outage. Start 23:32PT End 03:10PT
· Suite 709 – Power and network outage. Start 23:32PT End 00:50PT
· Suite 402 – Limited network outage (some latency/packet loss issues). Start 23:32PT End 00:50PT
· Firewall Clients. Network outage. Start 23:32PT End 03:10PT
Ted Smith
SVP, Operations
PEER 1